Connecting the UPS to utility power
WARNING: To prevent injury from electric shock or damage to the equipment:
Plug the input line cord into a grounded (earthed) electrical outlet that is installed
near the equipment and is easily accessible.
Do not disable the grounding plug on the input line cord. The grounding plug is an
important safety feature.
Do not use extension cords.
1. Connect the input power cord from an intended load device to the IEC-320-C14 input power
receptacle on the UPS rear panel (INTL model only).
2. Connect the UPS power cord to a grounded utility power outlet. When the UPS is plugged in, the
batteries begin to charge. Power to the output receptacles designated for surge and battery backup
is not available until the unit is powered up.
For more information about receptacle control, see "Power management software ("HP Power Manager
features" on page 21)" .
Connecting devices to the UPS
CAUTION: Do not plug laser printers into the UPS output receptacles. The instantaneous current drawn by
this type of printer can overload the UPS.
Before connecting devices, verify that the UPS will not overload by checking that the ratings of the devices
do not exceed the UPS capacity. If the equipment rating is listed in amps, multiply the number of amps by
the selected output voltage to determine the VA.
After verifying that the UPS will not overload:
Connect the device power cords to the output receptacles on the rear panel of the UPS
(NA/JPN/TWN model).
-or-
Connect devices to the output receptacles on the rear panel of the UPS using the jumper cords
included with the UPS (INTL model).
Charging the UPS batteries
Allow the batteries to charge before putting the UPS into service.
IMPORTANT: Charge the batteries for at least 24 hours before supplying backup power to devices. The
batteries charge to:
90% of their capacity within 4 hours
100% of their capacity within 24 hours