IBM T400 Computer Drive User Manual


 
Updating the Firmware with an FMR Tape Cartridge
Attention: SCSI drives and Fibre Channel drives require different firmware
images.
To update the Ultrium 2 Tape Drives firmware from an FMR tape cartridge:
1. Ensure that the tape drive is unloaded.
2. Place the drive in maintenance mode by pressing the unload button three times
within a 1.5-second interval. The status light becomes solid amber, which
means that the drive is in maintenance mode.
3. Press the unload button once per 1.5 seconds until 2 displays, then press and
hold the button for 3 seconds. When C flashes, the drive is waiting for a
cartridge.
4. Insert the FMR tape cartridge. 2 flashes, the drive loads the updated firmware
from the cartridge, and the status light flashes amber. When the update
completes successfully, 0 displays and the cartridge automatically ejects.
The drive resets itself and automatically activates the new firmware.
If the update fails, an error code displays. To resolve the error, locate the code in
Table 15 on page 67.
46 IBM TotalStorage LTO Ultrium 2 Tape Drive