108 SPARC Enterprise T5440 Server Service Manual • June 2011
Related Information
■ “CMP and Memory Module Device Identifiers” on page 107
■ “Performing Node Reconfiguration” on page 159
Servicing FB-DIMMs
■ “Remove FB-DIMMs” on page 108
■ “Install FB-DIMMs” on page 109
■ “Verify FB-DIMM Replacement” on page 110
■ “Add FB-DIMMs” on page 113
■ “FB-DIMM Configuration” on page 113
■ “FB-DIMM Device Identifiers” on page 116
■ “FB-DIMM Fault Button Locations” on page 117
▼ Remove FB-DIMMs
Before you begin, complete these tasks:
■ Read the section, “Safety Information” on page 63.
■ Power off the server, using one of the methods described in the section, “Powering
Off the System” on page 67.
■ “Extend the Server to the Maintenance Position” on page 70
■ “Perform Electrostatic Discharge – Antistatic Prevention Measures” on page 73
■ “Remove the Top Cover” on page 73
■ “Remove a CMP/Memory Module” on page 104
Do the following:
1. If you are removing a faulty FB-DIMM, determine which FB-DIMM you want
to remove.
Four CMP/memory pairs
(full configurations)
XXXX
Configuration
CMP3
MEM3
CMP1
MEM1
CMP2
MEM2
CMP0
MEM0